Hi All,
If the Fan Filter Units (FFU's) are ceiling mounted in the clean room application and the conditioned (make up) air is introduced in the void ( plenum) above, how the differential pressure between the airlock and the room is maintained.
The FFU's operate as full re-circulation and ramping them up or down will not affect the dP.
The only way the dP can be maintained is the for make up air to be actually ducted into the rooms rather than introduced in the void above.
Is the above correct or am I missing something?
Have seen applications with different density of FFU's in the ceilings when walking from room to room, not clear why unless different clean room classes are to be maintained.
Regards