EPRI NMAC 7502 recommends DC Hi-pot (step test) as a periodic maintenance test for form-wound motors. But they don't recommend it for 460-volt motors (they don't provide any explanation).
It appears to me that NEMA requires AC hipot on new motors, including 460 volt. Why wouldn't dc hi-pot be a good maintenance test for 480-volt motors. Calculate max voltage per IEEE95 (~(1.5-2)x(1.7)x460vdc).. alhtough IEEE 95 scope states it's limited to testing at 5kv and above.. with foot-note that the "methods" have been found applicable to smaller machines.
Does anyone do periodic dc hi-pot for 480-volt motors? Is there some reason this test would be less useful or perhaps more destructive for 480v motors (as compared to 4kv or 13.2kv motor), assuming IEEE95 voltage is used?
It appears to me that NEMA requires AC hipot on new motors, including 460 volt. Why wouldn't dc hi-pot be a good maintenance test for 480-volt motors. Calculate max voltage per IEEE95 (~(1.5-2)x(1.7)x460vdc).. alhtough IEEE 95 scope states it's limited to testing at 5kv and above.. with foot-note that the "methods" have been found applicable to smaller machines.