Has anyone heard replacement of 115kV arrestors (MOV type) is required on a periodical basis?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Very interesting thread.electricpete said:Monotiring leakage current is simple IF provisions are provided when the arrester is installed (for example insulate lightning arrestor from transformer tank and run the ground connection in an insulated lead down to ground level for clamp-on check.
If you insulate the ground lead, then the voltage across the transformer insulation during a lightning surge will include the L·di/dt drop in the ground lead. This practice may make testing easier, but it reduces the protective margin on the transformer. Perhaps a spark gap between the arrester base and the tank could be used to limit the voltage.Monotiring leakage current is simple IF provisions are provided when the arrester is installed (for example insulate lightning arrestor from transformer tank and run the ground connection in an insulated lead down to ground level for clamp-on check.