nkn5
Electrical
- Dec 25, 2010
- 34
I have a 400V switchboard with two incomers : one from emergency diesel generator (400V) and second from main power (gas turbine power @11kV stepped down to 400V thru couple of other switchgear in the overall system).
I would like to have load transfer from emg incomer to the main power incomer with out interruption ( make before break)provided the two sources are synchronized. Can you give me any idea on these questions I have
1) How much time typically is required for this transfer to happen ?
2) What fault current rating should I consider for the bus ? As I am not running the sources in parallel I do not want to addup the fault currents from the two sources.
3) Do I need any additional equipment to do this? or the breakers / IEDs programmed are enough to do this ?
Can you also share any practical problems / issues you have seen in your experience in doing this.
Thank you
I would like to have load transfer from emg incomer to the main power incomer with out interruption ( make before break)provided the two sources are synchronized. Can you give me any idea on these questions I have
1) How much time typically is required for this transfer to happen ?
2) What fault current rating should I consider for the bus ? As I am not running the sources in parallel I do not want to addup the fault currents from the two sources.
3) Do I need any additional equipment to do this? or the breakers / IEDs programmed are enough to do this ?
Can you also share any practical problems / issues you have seen in your experience in doing this.
Thank you