I'm working on a project with a pan joist roof. It's a 60'x40' building. I took the measurements and it's 20" form with 5" ribs 25" o.c.. The depth of the ribs is 8" with a 3" topping for a total depth of 11". I don't know the amount of reinforcement so I assumed the minimum. According to the CRSI tables the joists have a factored allowable uniform load of 112 psf. they want to install a 900 pound RTU but I don't think it works. The joists have a 60 psf dead load and a 25 psf snow live load. The uniform load from the footprint of the RTU is 33 psf. This is a factored load of 164 psf, about 50 psf over the allowable. The two openings for the air ducts in the pan joists are no more than 21" wide, so they won't interfere with longitudinal joists.
First question is how to reinforce the existing ribs of the pan joists? I'm thinking of bolting an angle to the underside of the ribs under the load of the RTU. How would I provide the required resistance at the supports for the applied shear?
Secondly, When I frame out the openings in the pan joists for the ducts, I'll probably run some C3x4.1 normal to the pan joists and connect them to the longitudinal joists with L2x2 angles to transfer the loads. Should I also bolt a C3x4.1 longitudinally to the joists for reinforcement or is it not necessary.
The CRSI manual says that for small openings (ones that don't affect any joist, i.e. narrower than the width of the rib) no reinforcement is required, but for a 21" wide opening (1" wider than the pan joist form) some of the joist may get cut, so I'm debating on whether or not to use the channels?
Your input would be appreciated.
Thanks
First question is how to reinforce the existing ribs of the pan joists? I'm thinking of bolting an angle to the underside of the ribs under the load of the RTU. How would I provide the required resistance at the supports for the applied shear?
Secondly, When I frame out the openings in the pan joists for the ducts, I'll probably run some C3x4.1 normal to the pan joists and connect them to the longitudinal joists with L2x2 angles to transfer the loads. Should I also bolt a C3x4.1 longitudinally to the joists for reinforcement or is it not necessary.