In last week, one of my friends asked me about his problem that occurred in his work as fellow. Actually, it was beyond my knowledge and I am much appreciate if anyone can solve his problem.
Thanks with regards.
thureinaung27
" During commissioning of the standby generator power system, a problem was identified with mal-operation of earth fault protection on each of the generators. There appeared to be no earth fault mal-operation problems when the system was operating from the mains utility power supply. The standby power system comprised three diesel generators operating in parallel supplying the 11kV site distribution network. When the generators were operating the system, neutral was earthed via a resistor bank. It was noticed that during the operation of the plant, prior to the earth fault protection operating, the resistors were getting very hot - exceeding their thermal rating - even when the generators were not fully loaded ".
Thanks with regards.
thureinaung27