Bung
Electrical
- Feb 10, 2002
- 428
I am having problems with a particular model of auto-recloser failing to operate under fault conditions, and instead the upstream protection operating. The picture is this: Single transformer 33/11kV substation, 5MVA, Dyn. Single incoming 33kV line, 33kV CB with overcurrent protection (IDMT, BS142 std inverse). Transformer has harmonic restrained biassed differential protection. Two 11kV feeders, each with the same type of recloser CB and contoller. The CB is KFME, controller is Form 4C. The reclosers are mounted on spun concrete poles in the substation yard. Earthing appears to be in accordance with the book. Auxiliary volts come from an aux transformer in the substation, connected at 11kV.
The problem: Occasionally (NOT every time) a fault on a feeder(no pattern to the type) will not be tripped by the recloser, but is seen and cleared by the transformer HV overcurrent. The recloser has been found open on at least one occasion after the 33kV protection cleared the fault. There is no transfer tripping or inter-tripping scheme. The recloser behaves perfectly in the lab. There is plenty of grading margin. Records from the Form 4C and the waveforms recorded by the 33kV protection indicate that the F4C should have cleared the fault with a margin of around 600msec.
Anybody got any ideas? Leprechauns sound good at the moment ...
Bung
The problem: Occasionally (NOT every time) a fault on a feeder(no pattern to the type) will not be tripped by the recloser, but is seen and cleared by the transformer HV overcurrent. The recloser has been found open on at least one occasion after the 33kV protection cleared the fault. There is no transfer tripping or inter-tripping scheme. The recloser behaves perfectly in the lab. There is plenty of grading margin. Records from the Form 4C and the waveforms recorded by the 33kV protection indicate that the F4C should have cleared the fault with a margin of around 600msec.
Anybody got any ideas? Leprechauns sound good at the moment ...
Bung