MAQs

Status
Not open for further replies.

CHMM-CSP

Civil/Environmental
Sep 1, 2020
3
thread184-245252

I have a question regarding the MAQs and increased volumes allowed with sprinklered spaces and storage in flammable storage cabinets. For example, if I have a class IB flammable liquid with a MAQ of 120 gallons for storage. If the room where I'm storing is sprinklered, that means I can store 240 gallons. If the room is sprinklered and I can store in flammable storage cabinents, can I double the amount again to 480 gallons?
 
Replies continue below

Recommended for you

Yes, so it's basically four times the basic quantity of 307.1(1).
 