Marx Generator

Status
Not open for further replies.

Cerkit

Electrical
Jan 18, 2016
100
Hi,

Does anyone have any practical experience with testing equipment using a Marx Generator. Given that one of the poles is earthed does this mean that the terminals need to be swapped over several times in order to ensure that all phases get tested to their full impulse voltage?

Thanks
 
Replies continue below

Recommended for you

Cerkit dear, you will need a high voltage probe with specifications that your pulse out rise time and duration are not affected by the probe specifications. Then a oscilloscope should be sufficient to do the measurement provided its bandwidth serves pulse parameters.
Hope it works, please feel free to discuss if any ambiguities exist
 