boffintech
Civil/Environmental
- Jul 29, 2005
- 469
The structure is masonry stem wall: footing with two courses of block placed so that top of course #2 is top of slab-on-grade and block is used as form for the SOG. Job specs call for these bottom two courses of block to be filled with "3000psi 3/8" pea gravel mix".
The contractor failed to request a masonry inspection until AFTER all the stem walls and SOG were placed. Upon arrival to the site the inspector found all the stem walls poured solid with concrete, apparently the same concrete that went in to the SOG. The contractor almost claimed that the pea gravel mix was used but realized they didn't have an approved mix ID or any delivery tickets for any pea gravel mix.
The inspector dutifully notified the EOR of this discrepancy and was told not to worry about it because those two courses of block were below grade but that the rest of the block had to have the correct pea gravel mix.
Clearly the SOG concrete mix will not meet the requirements of ASTM C476 and clearly NONE of that masonry work was inspected according to the schedule of special inspections either before or during construction.
Why is OK to use the SOG mix as block fill below grade and what happened to the requirements for inspection?
The contractor failed to request a masonry inspection until AFTER all the stem walls and SOG were placed. Upon arrival to the site the inspector found all the stem walls poured solid with concrete, apparently the same concrete that went in to the SOG. The contractor almost claimed that the pea gravel mix was used but realized they didn't have an approved mix ID or any delivery tickets for any pea gravel mix.
The inspector dutifully notified the EOR of this discrepancy and was told not to worry about it because those two courses of block were below grade but that the rest of the block had to have the correct pea gravel mix.
Clearly the SOG concrete mix will not meet the requirements of ASTM C476 and clearly NONE of that masonry work was inspected according to the schedule of special inspections either before or during construction.
Why is OK to use the SOG mix as block fill below grade and what happened to the requirements for inspection?