I have a high foundation wall (27'). I have a basement floor framed in so that it's unbraced for approx 17'. I don't remember my reinforcing because I did this a while back. I called out for truss-type joint reinforcing at every other coursing, and spec'ed for ACI 530.1 and ASCE 6 for materials and workmanship.
Ok, here is my delimma:
Ladder reinforcing was used by the contractor instead of truss-type.
I can EASILY slide a credit card (this is great to do because it destroys the magnetic strip thereby making it unusable! Use your wife's) between the webs of the blocks between coursings.
I designed for 10' of maximum backfill and show "10' max. backfill" on the plans. He has 14'.
Obviously the contractor has not built the wall per my plans and specifications. I'm writing a letter to outline this and basically not standing behind the wall (I'm a structural engineer! I stand beside my structures! (Not under them! )) due to these shortcomings.
Do I tell him the wall needs to come down?
Do I CC the building department on this letter?
Ok, here is my delimma:
Ladder reinforcing was used by the contractor instead of truss-type.
I can EASILY slide a credit card (this is great to do because it destroys the magnetic strip thereby making it unusable! Use your wife's) between the webs of the blocks between coursings.
I designed for 10' of maximum backfill and show "10' max. backfill" on the plans. He has 14'.
Obviously the contractor has not built the wall per my plans and specifications. I'm writing a letter to outline this and basically not standing behind the wall (I'm a structural engineer! I stand beside my structures! (Not under them! )) due to these shortcomings.
Do I tell him the wall needs to come down?
Do I CC the building department on this letter?