jeffhed
Structural
- Mar 23, 2007
- 286
I have a masonry building where the jambs on each side of some roll up doors are 32" wide and each cell is reinforced with (2) #5 bars to increase my "d" for both positive and negative wind pressures. I typically design this as a wall segment and do not require ties around the jamb reinforcing. The plan reviewer has stated that it is best practice to install lateral ties enclosing the vertical jamb reinforcing as if it was a column. I have looked through all of our textbooks here and the NCMA Teks as well as ACI 530 and can't find anywhere where it states that ties would be required. The jamb vertical steel has been neglected in determining allowable axial stresses and the jamb element has been designed using p-delta effects. My axial stresses are 50% of allowable and my combined stress check works but is close to 1. Are ties really required or is it considered best practice by the reviewing firm that may be considered overkill by many others? The only document I can find that addresses jamb reinforcing is an old document Army TM-5-809-3 (from 1992). Design example 3 on page 6-7 through 6-10 shows a jamb reinforcing design example. The design example shows (4) #6 bars vertical but does not require any lateral ties. I have talked to an engineer that works for a masonry manufacturer that says ties are not very typical. I have also talked to another plan reviewer I know and he said he has seen ties but they are not necessarily on every project. So I have decided to take a poll here. Does masonry jamb reinforcing require lateral ties for confinement?