par060

Structural
Feb 28, 2001
146
I have a steel framed building that is going to have a 10" CMU wall as its exterior. The design of the wall requires some tie back to the steel framing. I have seen a few details of dovetail type anchors used to do this but I havent seen any thing that gives capacities....I am sure they have to be fairly close together but I am lacking in experiance in designing this attachment..I am unsure how these anchors stay in the wall it seems they would "punch" thru the mortar....any help would be appreciated...
 
Replies continue below

Recommended for you

I don't know about dove tail, but I recently had Dayton Superior develop capacities for me on some of their light gage hooked anchors for the same kind of application. I would contact them.
 
Thanks haynewp....It seems this must be a fairly typical connection it could be a hook or dovetail...I just need something that supports the masonry wall from wind loads..tension and compression. I would like to see something that shows how this attachment stays fastened to the wall....some of details I have seen appear to be just set in between courses so the mortar holds it in.
 
You could run a bond beam at the elevation of the connection with embed anchors. The anchors could attach to a vertical slotted connection in the steel back-up to allow for deflection of the steel beam.
 