jmw
Industrial
- Jun 27, 2001
- 7,435
Re posting here since I got no wehere in the other forum....
This is a problem I came up with when reviewing bunkering. I've posted in Linkedin but I know I'll get the usual people chiming in about how wonderful coriolis meters are and touting fuel additives etc. so better here....
I have a problem understanding why things are done the way they are and some confusion.
I am looking at the quantity calculation during bunkering and let's assume we have measured the "observed" volume (commonly by tank dipping) - the volume of fuel at the fuel temperature which is also measured.
Typically we also have the base density as declared in the supplier's BDN and from prior lab analysis.
The calculation steps appear to be:
calculate the VCF (Volume correction factor) and convert the observed volume to standard volume (the volume at 15C).
Now multiply base density and standard volume to get the mass.
OK so far? But why that way round?
Surely it is better to:
take the base density and fuel temperature and calculate the alternative density - the density at the fuel temperature
then simply multiply observed volume and alternative density to get mass?
Same thing? not really.
The kicker is the VCF.
The VCF is effectively calculated by finding the alternative density anyway (density at fuel temperature) and using the ratio of base density and alternative density to find the VCF and then using the VCF to find the standard volume.
This involves the density in several different and unnecessary steps if we follow this sequence. And if the density is wrong, and in about 50% of cases where the commercial sample is analysed and compared to the BDN value there is a significant difference, what then?
Suppose we now measure density online.
This gives us the observed density directly (equivalent to the alternative density calculated from the base density, but measured directly and it has the advantage of being the true density value).
Technically one supposes one has to find the base density from the observed density, calculate the VCF and then the standard volume so one can again multiply the standard volume by density to get mass.
This seems to be how it has to be done since this is how the calculations are set out, including in various software solutions for bunkering which don't allow for alternative calculation procedures.
But it seems cumbersome, unnecessary and more vulnerable than simply multiplying the observed density and observed volume together to get the mass in one calculation step.
And, if we are to move increasingly to flow measurement, using observed values would seem a logical approach (assuming we use volumetric flow meters).
Bunkering is not unique in this. This procedure of converting everything to base or standard values seems quite a common way to do things......?
But suppose we have to apply the same logic to coriolis meters?
They measure "observed" mass, observed density (some of them with suitable accuracy) and the temperature.
Should they then:
Find the observed volume from the observed density and mass
Calculate the base density
Calculate the VCF
Find the standard volume
Multiply standard volume by base density to find the mass?
It is about as sensible, it seems to me, as the steps we do take.
So if it is done the way it is, there must be a good reason that I haven't understood, yes?
Oh, and it doesn't stop there.
Once we have the mass, by whatever means, we have to apply the weight correction factor to find the weight.
Why?
What is wrong with mass?
Oh, and does the coriolis meter apply the weight correction automatically or is it applied subsequently?
There are some other issues here but this is enough to be going on with I think.
JMW
This is a problem I came up with when reviewing bunkering. I've posted in Linkedin but I know I'll get the usual people chiming in about how wonderful coriolis meters are and touting fuel additives etc. so better here....
I have a problem understanding why things are done the way they are and some confusion.
I am looking at the quantity calculation during bunkering and let's assume we have measured the "observed" volume (commonly by tank dipping) - the volume of fuel at the fuel temperature which is also measured.
Typically we also have the base density as declared in the supplier's BDN and from prior lab analysis.
The calculation steps appear to be:
calculate the VCF (Volume correction factor) and convert the observed volume to standard volume (the volume at 15C).
Now multiply base density and standard volume to get the mass.
OK so far? But why that way round?
Surely it is better to:
take the base density and fuel temperature and calculate the alternative density - the density at the fuel temperature
then simply multiply observed volume and alternative density to get mass?
Same thing? not really.
The kicker is the VCF.
The VCF is effectively calculated by finding the alternative density anyway (density at fuel temperature) and using the ratio of base density and alternative density to find the VCF and then using the VCF to find the standard volume.
This involves the density in several different and unnecessary steps if we follow this sequence. And if the density is wrong, and in about 50% of cases where the commercial sample is analysed and compared to the BDN value there is a significant difference, what then?
Suppose we now measure density online.
This gives us the observed density directly (equivalent to the alternative density calculated from the base density, but measured directly and it has the advantage of being the true density value).
Technically one supposes one has to find the base density from the observed density, calculate the VCF and then the standard volume so one can again multiply the standard volume by density to get mass.
This seems to be how it has to be done since this is how the calculations are set out, including in various software solutions for bunkering which don't allow for alternative calculation procedures.
But it seems cumbersome, unnecessary and more vulnerable than simply multiplying the observed density and observed volume together to get the mass in one calculation step.
And, if we are to move increasingly to flow measurement, using observed values would seem a logical approach (assuming we use volumetric flow meters).
Bunkering is not unique in this. This procedure of converting everything to base or standard values seems quite a common way to do things......?
But suppose we have to apply the same logic to coriolis meters?
They measure "observed" mass, observed density (some of them with suitable accuracy) and the temperature.
Should they then:
Find the observed volume from the observed density and mass
Calculate the base density
Calculate the VCF
Find the standard volume
Multiply standard volume by base density to find the mass?
It is about as sensible, it seems to me, as the steps we do take.
So if it is done the way it is, there must be a good reason that I haven't understood, yes?
Oh, and it doesn't stop there.
Once we have the mass, by whatever means, we have to apply the weight correction factor to find the weight.
Why?
What is wrong with mass?
Oh, and does the coriolis meter apply the weight correction automatically or is it applied subsequently?
There are some other issues here but this is enough to be going on with I think.
JMW