cyriousn
Electrical
- Jul 19, 2017
- 24
I'm reviewing a project where there is a 270MVA 161/34.5kv transformer and no main circuit breaker on the 34.5kv bus. (I don't know of any circuit breaker for 34.5kv that is higher than 3000A which is a force air cooled switchgear breaker)
The 34.5kv bus has (8) 600A breakers. (7) of the breakers are connected to PV collector circuits and (1) is connected to a cap bank.
Is there any limit of how many circuit breakers can be on a 34.5kv bus without a main circuit breaker? I used to work in the commercial NEC realm so I keep thinking back to the 6 disconnect rule but I don't think that applies here. Any help here is much appreciated!