Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Max Amps?

Status
Not open for further replies.

joedirt9

Mechanical
Sep 23, 2011
33
Looking to determine the remaining capacity of an Immersion Heater:
480 V
90 kW
1-3 Phase

. The readings gave 67 Amps

Any ideas on how to determine the remaining capacity of this heater?

 
Replies continue below

Recommended for you

My crystal ball isn't working well today. [3eyes]

What is the nature of the supply - three phase star, three phase delta, line-neutral, or line-line?
How are the heater elements connected - some of them, all of them, series, parallel, star, delta, etc...?
How are they supposed to be connected to achieve rated output?
 
Not really, I used basic single phase and 3-phase power calculations that any engineer should know and a Google search would easily find.
 
well i was able to do that. but i am not sure that really gives a realistic evaluation of the heater. thanks alot though
 
No simple connection of a 90kW 3ph heater draws 67A. Nearest I could get was 62.5A for an element designed to be connected line-line (delta) but actually connected line-neutral (star). If the supply voltage is a little high then it's a possibility.

Without some of the additional details I requested before all any of us can do is guess.
 
i am working on getting some more info. thanks for sending me in the right direction scotty
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor