Hi All, first post on this forum. Please be gentle...
I have already checked the forum for similar topics etc...but I could not find exactly what I was looking for.
I am designing this king post wall with a retained height of 2.35m. This is going to be a garden wall inside a residential property and it will retain just garden so there are no roads, existing structures or services on the back of the wall. This is in UK.
Now I understand that there is not a specific max horizontal deflection limit to meet in the standards. I see also that in the CIRIA C760 says that for cantilever embedded walls a typical horizontal movement of 0.4% of the retained height is to be expected. This means in my case 9.4mm.
I understand also that the table 6.3 from CIRIA C760 is based on embedded walls with excavation that range in depth from 8m to 31m and I would like to hear from you what you think is a realistic horizontal limit. Am I overkilling the design if I use as a reference the CIRIA max horizontal deflection?
My top horizontal expected movement is about 17mm and before to change the design (reducing the spacing of the posts) I would like to hear your opinions regarding this.
Thank you for your help.