Max Velocity in Ducts

Status
Not open for further replies.

seadogg

Mechanical
May 5, 2003
1
Dear HVAC Experts:

What is the max desireable velocity one can size a duct for acceptable noise level ? Suppose the application is one where the ductwork is exposed in the conditioned space.
Thanks in advance for your help.

Seadogg
 
Replies continue below

Recommended for you

Hello,

Recommended velocities, FPM

Residence:
Main duct: 700-900
Branch duct: 600

Schools, Theaters, Public Bldgs:
Main duct: 1000-1300
Branch duct: 600-900

Industrial bldgs:
Main duct: 1200-1800

Obviously the duct velocities for the residence will give
the least noisy duct. You have to balance the cost against
the lack of noise.
Branch duct: 800-1000
 
Hello,

Recommended velocities, FPM

Residence:
Main duct: 700-900
Branch duct: 600

Schools, Theaters, Public Bldgs:
Main duct: 1000-1300
Branch duct: 600-900

Industrial bldgs:
Main duct: 1200-1800
Branch duct: 800-1000

Obviously the duct velocities for the residence will give
the least noisy duct. You have to balance the cost against
the lack of noise.
 