Maximum cantilever for CLT roof

efFeb

Structural
Dec 25, 2019
66
Hi! I am designing a roof with a significant CLT cantilever on one end. The deflection equations in the code are set up for a simple span beam. Does anyone have any guidance on maximum cantilever for a CLT panel, or for an approach to calculating the cantilever deflections (id expect that shear deformation would be much higher than for the simple span)

Thanks so much!
 
Replies continue below

Recommended for you

Is the cantilever causing in plane or out of plane bending? And which code excatly? IBC does allow you to consider two times the simple span deflection for cantilevers
 
Shear deformation is normally ignored. Take the normal cantilever deflection plus theta*Lc where theta is the backspan rotation due to the cantilever moment and Lc is the length of cantilever.

1732309971738.png
Google "Beam Diagrams and Formulas" and you will find several load combinations. The sketch above is for uniform load over the backspan and the cantilever.
 
Last edited: