Maximum velocity of water and foam mixture in pipes

Status
Not open for further replies.

Vijay93

Mechanical
Apr 28, 2020
8
HI,´

I am currently trying to hydraulically dimension pipes. I would like to know what is the maximum velocity to be used to determine the pipe sizes. 1 pipe has only water and the other has water and foam mixture (3% AFFF Foam). The application is Fire fighting.

Thank you for your help in advance.
 
Replies continue below

Recommended for you

What size nozzles are being used?

The acceptible flows depend on the hose or piping being used.

For liquids 3 m/s (10 ft/s) is commonly a maximum pipe velocity, depending on the fluid, etc.
 
If you look on this site you will find many posts.
There is no mandated "maximum".

3m/sec is a commonly used guide figure as a good balance between smaller pipe and higher pressure.

a lot depend son distance as well. Longer pipes - lower velocity is better, shorter ones you could have up to 5 or 7 quite easily and it makes only a few bar difference, but a smaller pipe.

If this is a fire system - see what NFPA say. They regulate everything to the nth degree. I think they give pipe sizes for certain max water flows.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
 
I don't know about NFPA, but in Europe, EN 12845 for automatic sprinklers does give a limit of 10 m/s in pipes and 6m/s through valves, flow meters and strainers.
 
Thank you all for your answers. I believe NFPA does not set a limit to maximum velocity but as mentioned EN 12845 sets the limit to 10m/s in pipes and 6m/s through valves, flow meters and strainers as mentioned by @HateMech
 
At some high flow the pressure drop may impact the foaming action.
Typically dP is the limit for flow in FP systems since use if so infrequent.
I believe that NFPA has flow limits for some devices, but as I recall they agree (nearly) with the EN values.

= = = = = = = = = = = = = = = = = = = =