milwaukeebob
Electrical
- Jun 21, 2004
- 42
Hello, first time user looking for some guidance. I am stationed at a combined-cycle power plant. An MCC which services our cooling tower experienced a major electrical fault during the start of one of the fan starters. The MCC bucket is no longer usable and needs to be replaced. The following are the relevant details so far:
(1) The fault occurred immediately when the fan starter received a start command.
(2) The fault appears to have originated on the load side of the bucket breaker prior to the contactor.
(3) The breaker did not trip when the fault occurred. Breaker was found in the CLOSED position.
(4) No unusual events occured prior to start of the fan.
(5) PI testing of the motor was initiated.Test result = 4.8
(6) Insulation resistance test of MCC bus was initiated. Test results = phase A (40 Gohms), phase B (22 Gohms), phase C (40 Gohms).
(7) Winding resistance to ground of motor was initiated. Test results ~ 30 Mohm for all phases.
(8) Except for the damaged bucket, the rest of the MCC line-up was returned to service and there have been no further incidences.
(9) The MCC and related equipment have been in service for approximately 2 years.
It is unclear what the root-cause of the failure is at the moment. Any experience with these type of failures and what we should be looking for? Thanks.
(1) The fault occurred immediately when the fan starter received a start command.
(2) The fault appears to have originated on the load side of the bucket breaker prior to the contactor.
(3) The breaker did not trip when the fault occurred. Breaker was found in the CLOSED position.
(4) No unusual events occured prior to start of the fan.
(5) PI testing of the motor was initiated.Test result = 4.8
(6) Insulation resistance test of MCC bus was initiated. Test results = phase A (40 Gohms), phase B (22 Gohms), phase C (40 Gohms).
(7) Winding resistance to ground of motor was initiated. Test results ~ 30 Mohm for all phases.
(8) Except for the damaged bucket, the rest of the MCC line-up was returned to service and there have been no further incidences.
(9) The MCC and related equipment have been in service for approximately 2 years.
It is unclear what the root-cause of the failure is at the moment. Any experience with these type of failures and what we should be looking for? Thanks.