MJK
Electrical
- Sep 10, 2001
- 5
I am supplying a 480VAC 3PH, 3Wire, No neutral MCC to an end user for connection to his distribution system. By contract the end user is responsible for the design and specification of his distribution system. The end user has reviewed and accepted my MCC specification, which does not include ground fault protection in this case. The MCC has a 1600A incoming breaker and controls several motors that require an orderly shutdown to avoid increased hazards due to the presence of liquid steel. NEC 230.95 states that GFP is required for each service disconnect rated 1000A or more, however exception 1 clearly states that GFP shall not apply if nonorderly shutdown will introduce additional or increased hazards. Question: Is the exclusion of GFP for the MCC in this case acceptable? If not, who should supply it. Thanks in advance.