MCC in Room with Piping

Status
Not open for further replies.

coloradog1

Mining
Apr 24, 2007
35
Can an MCC be installed in a room with an existing water pipe?
 
Replies continue below

Recommended for you

If in the US, see NEC 110.26(F)(1). As long as it is NOT in the required dedicated space.
 
Further, the pipe should not have a flanged joint in the switchgear room. This is to prevent the fluids splashing on to the panel in case of gasket problems etc.
 