davidbeach said:
That would be for an instantaneous (magnetic) only breaker. Generally different rules for breakers that also include the thermal element.
The magnetic (Instantaneous Trip or IT) elements are the same either way though if the breaker frame is the same, but the IT settings on any given breaker are never more than 10x the frame size. What using the different rules for a T-M breaker does for you is to allow a larger frame size, which will then have a higher setting available to use.
One reason it is difficult to pre-calculate the IT settings is that there are numerous factors that go into the instantaneous current. One of those is the magnetizing current at the instant the motor is connected. Studies have shown that can be as high as 2200% of the motor nameplate FLC. This is because in the very first instant the windings are connected, there is no inductance yet, only the resistance of the magnet wire in the windings. So the current will rise at the available fault current level, minus the conductor resistance. Depending on when in the sine wave that connection is made, that can last upward of 1/2 cycle, long enough to make a difference in the total inrush value seen by the magnetic elements. That's why I generally just use whatever works without nuisance tripping, up to (but not over) the legal limits. I don't sweat the details as to why it has to be that high, it's just too variable.
When people started experiencing this first hand is when motor manufacturers were forced to start increasing efficiency. They did so of course by reducing losses and one major way to accomplish that was to reduce the I
2R losses inside of the stator by reducing the winding resistance. So when "Energy Efficient" motors first started hitting the market in the mid 1980s, those used in replacing older motors began blowing fuses and tripping breakers on instantaneous even though the previous older motors had never given them any problems. Here in the US, the NEC had to add another exception to the IT settings for motor circuits, allowing for up to 1700% trip settings instead of the previous 1300% limit if it can be shown that the lower settings cause nuisance tripping. On EE motors, it almost invariably does.
"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington