MCCB single pole ratings

Status
Not open for further replies.

alehman

Electrical
May 23, 1999
2,624
UL 489 and IEC (I think) specify single-pole full voltage short circuit test current for three pole molded case circuit breakers which are much lower than the 3-phase interrupting rating. For example, 1200A frame 3-pole breakers are tested at 12.1kA for full voltage across one pole per UL, regardless of the marked AIC rating.

Corner-grounded systems require the ability for any one pole of a 3-pole breaker to interrupt faults at line-to-line voltage and 87% of rated interrupting current. Does anyone know of a manufacturer of MCCBs tested or rated for line-to-line voltage across a single pole?
 
Replies continue below

Recommended for you

You might want to check with Square D. I seem to recall that their breakers are tested for this.
 

It may be worth mentioning that, besides corner-grounded systems, midtap-grounded 480?/240-volt and 480-volt high-resistance-grounded systems also need the single-pole overcurrent withstand ratings applied.

Another related caveat is that 300-volt fuses applied to a corner-, midtap- or resistance-grounded 480-volt system is also a serious misapplication.
 
Thanks. I'll give SqD a call. This is an installation that one of my clients just finished. The breakers are GE type SKLB.

I think in the case of resistance-grounded or ungrounded systems, the situation can only occur if there are two L-G faults with one upstream and one downstream of the breaker.
 