UL 489 and IEC (I think) specify single-pole full voltage short circuit test current for three pole molded case circuit breakers which are much lower than the 3-phase interrupting rating. For example, 1200A frame 3-pole breakers are tested at 12.1kA for full voltage across one pole per UL, regardless of the marked AIC rating.
Corner-grounded systems require the ability for any one pole of a 3-pole breaker to interrupt faults at line-to-line voltage and 87% of rated interrupting current. Does anyone know of a manufacturer of MCCBs tested or rated for line-to-line voltage across a single pole?