A new Control Panel is fed by a 400A molded case circuit in a panelboard.
It was determined that the available fault current was about 9 kA at a new Control Panel. The SCCR of the panel is 5kA. So the Control Panel is under dutied for the available fault current.
A current limiting reactor is proposed. After installed the available fault current will be limited to 1kA. However, such low fault current on the 400A breaker eliminates the breaker instantaneous region on the breaker curve (the lowest setting is 2000A). Which in turn makes the arc-flash energy much higher.
Is there a remedy for this situation or is this just the trade off you must live with?
It was determined that the available fault current was about 9 kA at a new Control Panel. The SCCR of the panel is 5kA. So the Control Panel is under dutied for the available fault current.
A current limiting reactor is proposed. After installed the available fault current will be limited to 1kA. However, such low fault current on the 400A breaker eliminates the breaker instantaneous region on the breaker curve (the lowest setting is 2000A). Which in turn makes the arc-flash energy much higher.
Is there a remedy for this situation or is this just the trade off you must live with?