Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

MDS 520 Circuit Breakers

Status
Not open for further replies.

Kingstonrupp

Electrical
Oct 24, 2008
9
I have a situation where we have two 1.2MW Generators feeding a 5600A bus in parallel. The generator breakers are MDS 520 and have been specified as 2000AT/2000AF. I had a senior engineer go through the single line and he was concerned that having a 2000AT trip unit installed in the 2000AF breaker was a violation of the 80% rule in the code. I have since done some research on the breaker and found that they are actually rated for 100% continuous operation.

My question is, if a breaker manufacturer is fabricating CSA approved breakers that have trip units and frames sizes of the same value (i.e. 2000AT/2000AF) can we not assume that we are not in any violation of the code. My interpretation of the code CEC 8-104 is that your load and conductors should only be 80% rated if your breaker is not marked 100% or is marked 80%. I did not interpret this rule to indicate that you cannot install a 2000AT unit in a 2000AF breaker when they are designed to operate together by the manufacturer. The senior engineer wanted to change the breaker to 2000AT/2500AF if it was only 80% rated. Luckily it was 100% rated so no argument.

But even if the unit was 80% rated, I still would have argued that you can use a 2000AT unit in a 2000AF breaker, just that your load should be sized for no more than 1600Amps. Am I wrong on this?

Thanks in advance.
 
Replies continue below

Recommended for you

These trip units are calibrated to permit 100% amps rating. That said, the pick up value of the long time is set at 110%. No trip should occur below 2200 +/- 10%.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor