We had field measurements done by a company out of Ontario that measured, GPR, Grid R to remote earth, current split, Step & Touch Potentials using current injection. The instruments were all tied to a data recorder for near simultaneous measurements. They used a 55Hz generator to inject current and filtered all the results to eliminate any 60 Hz influence.
The substation's incoming line was not yet energized and could be safely grounded about 1.5 km away. Fault current was injected A phase to ground and current split measured in the OHGW, phase wires and the local distribution line neutral wires. Current was 10-15A. Step and touch voltages were measured at typical locations.
The measured split came out close to our calculated split. Step and touch came out better than predicted by CDEG's software. Test was expensive. The company claimed they do similar testing on energized substations and lines up to 230 kV. They developed the system when they were a part of Hydro One, the Ontario utility, and then became privatized. (I'm trying to find their name).