stookeyfpe
Specifier/Regulator
- Mar 13, 2005
- 1,882
I have a 7 story Group S-2 (parking garage), Group B (business office and amenities center) and Group R-2 (student housing) building under construction. I'm reviewing the shop drawing and calculations submittals. This is podium style construction where the 1st-3rd floors are IBC Type IA construction and floors 4-7 are 2015 IBC Type IIIA construction.
The fire protection contractor has noted that slabs are PT (post tension). The FP contractor has not provided the data sheet for the expansion anchors. For this and 23 other reasons the plans are not approved.
Frankly I kind of embarrassed to ask this question because PT construction is commonly employed in my jurisdiction and I know that 2015 IBC Table 1705.3 requires special inspections. However, I can see a scenario where the Structural Engineer of Record (EOR) may prohibit their installation. So the question is have any of you fine designers encountered this situation and do you RFI the Structural EOR? I'm of the belief I need documentation that the Structural EOR needs to allow the use of these type of anchors. We have no seismic design requirements in my jurisdiction.
I do know these anchors would be subject to Special Inspection. As to if this is happening is up to the Building Inspector.
As always I appreciate your candid analysis and opinions. Thank you for your time.
The fire protection contractor has noted that slabs are PT (post tension). The FP contractor has not provided the data sheet for the expansion anchors. For this and 23 other reasons the plans are not approved.
Frankly I kind of embarrassed to ask this question because PT construction is commonly employed in my jurisdiction and I know that 2015 IBC Table 1705.3 requires special inspections. However, I can see a scenario where the Structural Engineer of Record (EOR) may prohibit their installation. So the question is have any of you fine designers encountered this situation and do you RFI the Structural EOR? I'm of the belief I need documentation that the Structural EOR needs to allow the use of these type of anchors. We have no seismic design requirements in my jurisdiction.
I do know these anchors would be subject to Special Inspection. As to if this is happening is up to the Building Inspector.
As always I appreciate your candid analysis and opinions. Thank you for your time.