I have a room that holds about 10 pumps of all sizes, 3 chillers (2 centrifugal (R-123) , 1 Screw (R -134a), A HX, 6 VFD drives and A MCC in the central plant. When you design for a shut down or panic button is the intent on shutting down the Chillers themselves or is the intent on shutting down the Central plant as a whole? Keep in mind i have a Refigerant monitor Whith bells and whistles and a 24 hour operting ex fan for the emergency ventilation. I would think you would want the plant to shut down not just the chillers themselves. Any help would be appreciated

thank you
 
Replies continue below

Recommended for you

I thought panic buttons were for boilers and gas fire equipments etc in case of a fire or gas leak? Where I live it is hot and we never install boilers so never install panic buttons.

With electrical equipment the danger would be electrocution so a panic button should cut off all electrical supplies.

Note that suddenly cutting power to chillers does have potential for damaging the equipment!
 
The hazard is the chillers. No code requirement for shutting the pumps down that I am aware of.
 