looking for some help on MV Motor, the nameplate gives the following information
2900Kw, 991 Rpm, 11000 V Y, 991 rpm, 50 hz .085 cos, Rotor 1375 A
This motor has been working fine for 15 + years I'm told, I have only started working in this plant.
In the last 2 years, the motor has started burning brushes on one phase and not always been the same phase.
We looked at the trends and the motor seems to be working at 80% of its capacity, but the rotor amps is very low just 70-80 amps per phase. We do see one phase with approx 10-15% higher reading tot he others.
On this trend we also see the vibration rises from normal 1.2 m/s to 2.6-2.9 m/s which is still quite low. The motor will then trip and the brush will be burned out.
I would like to try and ask your opinion as to why you think the rotor amps are so low and to see why you think the brushes are burning.
Regards
F.E.G
looking for some help on MV Motor, the nameplate gives the following information
2900Kw, 991 Rpm, 11000 V Y, 991 rpm, 50 hz .085 cos, Rotor 1375 A
This motor has been working fine for 15 + years I'm told, I have only started working in this plant.
In the last 2 years, the motor has started burning brushes on one phase and not always been the same phase.
We looked at the trends and the motor seems to be working at 80% of its capacity, but the rotor amps is very low just 70-80 amps per phase. We do see one phase with approx 10-15% higher reading tot he others.
On this trend we also see the vibration rises from normal 1.2 m/s to 2.6-2.9 m/s which is still quite low. The motor will then trip and the brush will be burned out.
I would like to try and ask your opinion as to why you think the rotor amps are so low and to see why you think the brushes are burning.
Regards
F.E.G