Medium Voltage Contactors Short Circuit Protection 3

Status
Not open for further replies.

EECR7

Electrical
Jun 27, 2019
8
Is there a specific standard or industry practice that mentions how to protect medium voltage contactors against short circuits?
 
Replies continue below

Recommended for you

If you are talking about MV motor starters, the fuses in the starter are current-limiting. The opening of the contactor is generally delayed slightly to allow the fuse to clear the fault. 8 cycle dropout time was common at one time. This allows the fuse time to clear any fault that exceeds the interrupting rating of the contactor.
 