Medium Voltage Inductive Heating

Status
Not open for further replies.

nickoliver

Electrical
Aug 20, 2004
27
I thread in another forum has sparked my curiosity. The subject being the practice of utilities transitioning from overhead to underground (66KV) with the insulated (UG)cables entering a steel pole through individual holes. Since there is no mutual canceling of phases with this arrangement is there ever a problem with inductive heating? Does the shield around the cable have any effect in minimizing this?
 
Replies continue below

Recommended for you

Shielding on the cables is for voltage field control - NOT magnetic field control. It is entirely possible to use non-magnetic steels for a structural member and route all three phases, individually, through the same plate. Large transformers do this all the time.
 