a10j,
Your test measures the leakage current of an AC test? I have heard of this in laboratory but, it is very rare in my experience.
How a PD test works... That is short conversation but, a long written explanation, depending on what level you want to discuss the topic. The following is an overview from 10,000ft.
PD (a small micro arcing inside insulating material) is associated with the final breakdown mechanism of more than 99% of all extruded dielectric systems. This is why manufacturers have been using PD tests to prove the integrity of extruded dielectric components for the last 40 years. An AC voltage stress is applied to the system and if there is a defect it says ‘ouch’ in the form of PD activity at the defect site. If your detection system is sensitive enough (proven through a sensitivity assessment), the PD signal response can be measured and located. Once he defect is located you can determine if the defect is in the cable, joint, or termination and apply the appropriate component standard (IEEE 404 for joints, IEEE 48 for termination, IEEE 386 for separable connectors, and ICEA S-93-639 for MV cable insulation) to determine if it passes the standard.
StineIng,
For MV class (5k - 35kV) cable system tests we typically use a series resonant transformer (200-500kVA). HV class (69 -400kV) tests we typically use a frequency resonant transformers (1000kVA - 22MVA).
Regards,
Benjamin Lanz
Vice Chair of IEEE 400
Sr. Application Engineer
IMCORP- Power Cable Reliability Consultants