Francisco Mendonca
Hello, i am new here and i need help.
I am working on a 6900/400Volt, 225 KVA transformer, with 10 years of use, that feeds a pump house with 8 frequency drivers for 8 motors. This installation don´t have any filters for harmonics, caused by the frequency drivers. Our transformer is oversized for our building, a total of 8X 20KW for each motor, but only works a maximum of 4 pumps each time ( use to be only 2 pumps)
Our transformer is a class of temperature 65 °C. The actual temperature of it is between 70 and 80 °C and environment temperature use to be around 26 °C. We open it a few days ago to check for bad connections but none found. The oil had a bad smell so we replace it. after close it and connect it to the power lines, without any load, the temperature rise for 70 °C in 24 hours. voltage was 235 Volt in al the 3 phases to neutral and 407 Volts in all the 3 phases ( L1/L2, L1/L3 And L2/L3) Perfect except the heat. After connect 2 pumps, total 40 KW, the temperature is around 80 °C. Is this a normal temperature? If not what can we do to fix the issu?
Thank you very much
Mendonca
Thank you very much
Mendonca