Hello I am in charge of sizing and ordering substation batteries and chargers. I have run into a problem while trying to size the power cable between the 60 cell battery bank and the DC distribution cabinet. My company sizes the cable using the following formula.
(I/A)^2*t = .0297 * log [(T2 + 234)/(T1 + 234)] with the following values for the subscripts.
I = Short circuit current (specified by the battery manufacture)
A = Conductor cross sectional (in circular mils) (Value that is to be solved for)
t = time of short circuit (14 seconds)
T1 = Conductor Operating Temperature (75 C)
T2 = Maximum Short circuit Temperature (Temperature at which insulation is damaged)
I know by consulting NEMA WC5 that the conductor operating temperature for power cable is 75 C
I can’t find values for variable T2.
Would any forum be able to locate the melting temperature for polyethylene insulation? Is this temperature standard for most power cable manufactures?
Thank you for your assistance
y
(I/A)^2*t = .0297 * log [(T2 + 234)/(T1 + 234)] with the following values for the subscripts.
I = Short circuit current (specified by the battery manufacture)
A = Conductor cross sectional (in circular mils) (Value that is to be solved for)
t = time of short circuit (14 seconds)
T1 = Conductor Operating Temperature (75 C)
T2 = Maximum Short circuit Temperature (Temperature at which insulation is damaged)
I know by consulting NEMA WC5 that the conductor operating temperature for power cable is 75 C
I can’t find values for variable T2.
Would any forum be able to locate the melting temperature for polyethylene insulation? Is this temperature standard for most power cable manufactures?
Thank you for your assistance