Are most medium voltage metal-clad switchgear enclosures located in a controlled environment(indoors) specified as NEMA 1?

Thanks,
EE
 
Replies continue below

Recommended for you

You can get outdoor metal-clad switchgear. But it's a little different in that there is another enclosure around the switchgear, with an aisle in the front or down the middle (depending on the size). Metal-clad switchgear has to allow access to the back for making connections, if you put it outdoors, working on it in the rain becomes problematic.
outdoor_switchgear.jpg


As a general rule however, switchgear is not referred to by the NEMA designations for enclosures like NEMA 1 or NEMA 3R etc. It's just referred to as "indoor" or "outdoor".


" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
 