AmitDarwhekar
Electrical
- Dec 5, 2011
- 1
Hi All,
I have a 4200:120 open delta metering PT, which gives following voltage measurements when the voltage is measured phase to phase on the secondary side of the PT: Vab = 118.8 (4160), Vbc = 119.4 (4180), and Vca = 120(4200). I know that the voltages typically differ marginally on all three phases but they all should be more or less the same. Has anyone encountered this issue before where phase-phase readings are different on all three phases?
Just to give you guys background, I have a Basler DECS-100 voltage regulator that controls the voltage. A +/-3V bias signal is provided from Woodward Easygen 3200 controller to the regulator. When I monitored the bias signal, I noticed that once the voltage reaches 4160V on phase AB, the bias signal stays fairly steady in the range of 53.12% to 53.26%. According to Woodward tech. support Easygen only looks at the phase AB voltage for controlling the bias signal. Since I am reading 4160V on phase AB, Easygen does not try to bring the voltage down even though my average voltage is higher than my actual voltage set point. Further, presently I don't have any load on the generator.
I am fairly new when it comes to troubleshooting transformer related issues. I would appreciate few hints from where I can start troubleshooting this issue.
Thanks and Regards,
Amit
I have a 4200:120 open delta metering PT, which gives following voltage measurements when the voltage is measured phase to phase on the secondary side of the PT: Vab = 118.8 (4160), Vbc = 119.4 (4180), and Vca = 120(4200). I know that the voltages typically differ marginally on all three phases but they all should be more or less the same. Has anyone encountered this issue before where phase-phase readings are different on all three phases?
Just to give you guys background, I have a Basler DECS-100 voltage regulator that controls the voltage. A +/-3V bias signal is provided from Woodward Easygen 3200 controller to the regulator. When I monitored the bias signal, I noticed that once the voltage reaches 4160V on phase AB, the bias signal stays fairly steady in the range of 53.12% to 53.26%. According to Woodward tech. support Easygen only looks at the phase AB voltage for controlling the bias signal. Since I am reading 4160V on phase AB, Easygen does not try to bring the voltage down even though my average voltage is higher than my actual voltage set point. Further, presently I don't have any load on the generator.
I am fairly new when it comes to troubleshooting transformer related issues. I would appreciate few hints from where I can start troubleshooting this issue.
Thanks and Regards,
Amit