I've got a strange one now...
Lynn MII Main stop valve. This is the constant orifice feed, and servo drain to close.
When the valve is opened, it will not go closed the last inch. The valve can be fully opened, then asked for closed and it travels smoothly, but stops 1" from closed.
When tripped (even from 1" open position) the valve will close.
When reset, it stays closed until servo current is brought to null
The cabinet is putting 40mA on 16mA servo (415). I've used a voltage source for VPU error to drive it with varying current levels
I've replaced servos twice, (used on of those on the IV scram and it worked there)
I've checked the feed orifice, drawing 0.040". I found 0.043 and installed a 0.032"
The smaller orifice did make a difference in opening time, but not in the 1" from closed stopping
I've checked the servo jet tubing
I've verified the actuator spring wire diameter, coils, and pitch are the same as the RSVs (and the same as sister unit)
The drain to the tank does not go through the coolers
I'm requesting a pressure guage installed to measure hystersis today and minimun pressure with maximun servo drain
Every had any thing similar or any suggestions?
Lynn MII Main stop valve. This is the constant orifice feed, and servo drain to close.
When the valve is opened, it will not go closed the last inch. The valve can be fully opened, then asked for closed and it travels smoothly, but stops 1" from closed.
When tripped (even from 1" open position) the valve will close.
When reset, it stays closed until servo current is brought to null
The cabinet is putting 40mA on 16mA servo (415). I've used a voltage source for VPU error to drive it with varying current levels
I've replaced servos twice, (used on of those on the IV scram and it worked there)
I've checked the feed orifice, drawing 0.040". I found 0.043 and installed a 0.032"
The smaller orifice did make a difference in opening time, but not in the 1" from closed stopping
I've checked the servo jet tubing
I've verified the actuator spring wire diameter, coils, and pitch are the same as the RSVs (and the same as sister unit)
The drain to the tank does not go through the coolers
I'm requesting a pressure guage installed to measure hystersis today and minimun pressure with maximun servo drain
Every had any thing similar or any suggestions?