Ibeam
Structural
- Sep 12, 2001
- 42
My question is about frost depth requirements for an outdoor industrial slab on grade. Minimum ftg depth for frost penetration is 24 inches. Slab size is 70 x 80 ft.
I have numerous pieces of equipment – tanks, pumps, platforms, pipe supports, vessels, all light to moderate loadings in that the highest pressure under the slab from any one item may be 1000psf.
I would like to support all of this with a thickened slab and pedestals (heights of 12 to 18 inches for the pedestals). The slab perimeter will only be inches above grade, and the thickened edge will rest on a separately poured stem wall (10”x 2’ depth). The base requirements for such a situation per the soils report calls for 3-ft. of type-a aggregate material compacted to 95% std. Proctor. The existing soil is uncontrolled fill material and expansive. The fill depth reaches down to 18 ft.
Using this method, the Client does not think the minimum ftg depth requirement due to frost has been met and that the slab could heave at the inner areas. My thinking is that the base material will prevent the water from penetrating to form ice lenses in addition to the 3’ concrete depth at the perimeter keeping surface water from getting under the slab. Is this a sound theory?
I have numerous pieces of equipment – tanks, pumps, platforms, pipe supports, vessels, all light to moderate loadings in that the highest pressure under the slab from any one item may be 1000psf.
I would like to support all of this with a thickened slab and pedestals (heights of 12 to 18 inches for the pedestals). The slab perimeter will only be inches above grade, and the thickened edge will rest on a separately poured stem wall (10”x 2’ depth). The base requirements for such a situation per the soils report calls for 3-ft. of type-a aggregate material compacted to 95% std. Proctor. The existing soil is uncontrolled fill material and expansive. The fill depth reaches down to 18 ft.
Using this method, the Client does not think the minimum ftg depth requirement due to frost has been met and that the slab could heave at the inner areas. My thinking is that the base material will prevent the water from penetrating to form ice lenses in addition to the 3’ concrete depth at the perimeter keeping surface water from getting under the slab. Is this a sound theory?