In my area (Northeast US) I do not typically see two way elevated slabs less than 8". Do others see/use less than this and if so what is a lower bound? I would think that 6" is pretty thin once tolerances and unknowns are accounted for, i.e. the 'd' being off by 1/2" in the field is a much larger percentage at 6" slab compared to 8". 7"?
 
Replies continue below

Recommended for you

For a 6 inch slab to work the column spacing would have to be about 18 ft (l/36; 60 ksi bar; drop panels), but it seems as a practical matter (closely spaced columns; drop panels practically on top of each other; and the reasons you state above), that someone would have to be trying to make that work. I've never used less that 8 inches.
But I bet you'll get a response from womeone who does it all the time.
 
I'm assuming no drop panels as they are not typical here.
 
Take a look at section 9.5.3.3of ACI 318-11.

there are equations in that section for minimum thickness h between supports.
 
Yes but 9.5.3.4 allows different values as long as deflections are computed. Even using the table, assuming no drops and no beams w/Fy=60, then a 7" slab is good for 17.5 clear span (so say ~19' c-c). Running the fea probably pushes that a little further. Was just curious if anyone is using less than 8" since it seems to work by calculation for many situations.
 
I've used 7" and 7.5" often for residential floor plates. That's the minimum that I feel comfortable putting conduit etc in and it's tight at that.

The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
 
I have used 7" and 7.5" slabs on 28-30 ft spans, with careful studies of long-term deflections
 
I've gone 6" for parking slabs and 7" for retail.
 
The thinnest slab I have been involved in (on repair, not design) was a 4-1/2" PT slab, with a 3/4" set down/depression at exterior balconies, so at the edge anchorages it was 3-3/4" thick. Slab spans were short, and they were one-way spanning, not 2-way.

It was most ridiculous slab design I have ever seen - design was probably dated early 1970's. We were tasked with repairs to corroded PT anchorages, and destressing was undertaken by chipping concrete behind the live-end anchorages. Bastard of a project.

I have a distaste for VERY thin slabs, be it RC or PT.
 
I have gone to 150mm slab supported on walls.

"Programming today is a race between software engineers striving to build bigger and better idiot-proof programs, and the Universe trying to produce bigger and better idiots. So far, the Universe is winning."
 
I have done a few alterations and additions on buildings from the 30s,40s and 50s

These often have 4 1/2", sometimes even 4". Supported on beams/walls though, not columns.

I've also come across really thin one way ribbed slabs from that era. 2.5" spanning one way between the ribs with a central layer of mesh, 2.5" wide ribs with a single bar bottom, and no shear reinforcement.



We specify 150mm slabs all the time.
 
bookowski,
My approach to selection of flat plate thickness is to consider punching shear first. This of course involves spans and column sizes, but if a flat plate works in punching shear, it will usually work in bending strength and serviceability.
 
We've done a bunch of 6" slabs but those were all short spans in both directions. For anything of real size we start at 7 or 8.
 
Thanks for the input - exactly what I was looking for.
 