Hi All,
Has anyone had or heard of a miniature ABB 2 pole breaker failing?
I was in Mexico last week commissioning our equipment that has a number of ABB miniature breakers installed in the Control Cubicle.
On switching on the main 200A/480V disconnect, also in the control cubicle. There was a loud explosion caused by a flash over between terminals on the two incoming phases of a 3A ABB miniature breaker. The resultant carbon/copper etc. blew downwards and onto the terminals of a 3phase terminal block which caused a further short circuit on all three phases.
Luckily we have current 150A current limiting fuses in the disconnect so at least this limited the fault current. They in fact ruptured before the breaker at the substation tripped.
I should also say that while the humidity was high around 80% the whole cabinet and all equipment was very clean and no condensation was apparent anywhere.
We will have to renew both the 2 pole breaker and the terminal block as the blackening is extensive. As a result of this, I am a little wary of installing a new breaker, although we have used this type of breaker in many of our units previously.
Any previous experience or comments would be appreciated.
Has anyone had or heard of a miniature ABB 2 pole breaker failing?
I was in Mexico last week commissioning our equipment that has a number of ABB miniature breakers installed in the Control Cubicle.
On switching on the main 200A/480V disconnect, also in the control cubicle. There was a loud explosion caused by a flash over between terminals on the two incoming phases of a 3A ABB miniature breaker. The resultant carbon/copper etc. blew downwards and onto the terminals of a 3phase terminal block which caused a further short circuit on all three phases.
Luckily we have current 150A current limiting fuses in the disconnect so at least this limited the fault current. They in fact ruptured before the breaker at the substation tripped.
I should also say that while the humidity was high around 80% the whole cabinet and all equipment was very clean and no condensation was apparent anywhere.
We will have to renew both the 2 pole breaker and the terminal block as the blackening is extensive. As a result of this, I am a little wary of installing a new breaker, although we have used this type of breaker in many of our units previously.
Any previous experience or comments would be appreciated.