Minimum Conc. Column Size

Status
Not open for further replies.

STR04

Structural
Jun 16, 2005
187
Are there any ACI provisions for minimum (tied) column width? I'm trying to match 8 inch CMU with an 8x16 column and I know it not the easiest to construct with 1.5 inch clearance. Would there be an opportunity to reduce the cover to 3/4 inch, similar to a conc. wall. I wonder what the tilt-up association uses for tied wall piers/columns.

TIA
 
Replies continue below

Recommended for you

Check the section on slenderness effects in compression members in ACI 318.
 
Be careful with your fire ratings on a column that small as well.
 
I've gone down to 10" columns in stairwells - but not smaller - you'd have trouble getting your ties to fit and your vertical bars get so bunched together that you might have trouble getting concrete consolidated below.

 
We have 8-inch wide columns on many projects. They're a pain but possible.
 