ruchira2580
Structural
- Sep 20, 2017
- 9
According to the standard EC2, It states that the minimum horizontal reinforcement of a wall to be greater of 25% of vertical reinforcement or 0.1Ac% in each face. I have attached the detailing manual code for the reference for this clause published by Istruct. But it seems like it is really unrealistic in case of high rise buildings with lengthy shear walls.
For an example let's consider a RC wall having 450x2500 mm dimensions having H40@125 c/c (per 1m length) (As= 10053 mm2/m) . So according to this standards The minimum horizontal reinforcement comes as,
Max(450x2500x0.1/100 , 10053*0.25) = Max( 1125, 2513) = 2513 mm2/m which is a larger value per face, need at least T20 horizontal bars at 100 mm c/c(Asv = 3142 mm2/mm)per face. T20 links with 100 mm means a lot.
Is this minimum is correct or I have misinterpreted it...Please explain???thanks
For an example let's consider a RC wall having 450x2500 mm dimensions having H40@125 c/c (per 1m length) (As= 10053 mm2/m) . So according to this standards The minimum horizontal reinforcement comes as,
Max(450x2500x0.1/100 , 10053*0.25) = Max( 1125, 2513) = 2513 mm2/m which is a larger value per face, need at least T20 horizontal bars at 100 mm c/c(Asv = 3142 mm2/mm)per face. T20 links with 100 mm means a lot.
Is this minimum is correct or I have misinterpreted it...Please explain???thanks