Minimum outside air on VAV

Status
Not open for further replies.

remp

Mechanical
Sep 15, 2003
224
Hello,

Does anyone have a genuine control strategy to control and maintain minimum outside air on a VAV system?

Thanks!
 
Replies continue below

Recommended for you

Having a separate minimum outside air and variable air louver seems to have worked best for me, and is a lot easier on TAB contractors.
 
you can use OA reset with a CO2 sensor in return.
Even better would be to use an ERV for ventilation, that would equal the above injection fan.
 
Consult the rooftop manufacturer, they have the best knowledge of their product and product control.
 
Are you asking about ensuring the minimum OA gets into the air handler, or that the min OA reaches each individual space served by a VAV box?
 
The ventilation calculations have a very good hold on this question. 62MZCalc, while a little difficult to initially understand, does a fabulous job in illustrating the amount of outside air at the design condition. And the International codes follow the same path, with differing equations to a point.

My main question would be, can you supply 30% of air to the space for heating (see ASHRAE 90.1) and still maintain the minimum outside air required?
 
Have the VAV return fan track the VAV supply air fan with constant differential equal to the minimum OA CFM. You need airflow measuring station at the supply & at the return. Consider Air Monitor airflow measuring stations at each fan inlet.
 
Calculation is more important and more complex than control strategy. You have to size VAV units to both provide cooling and fresh air in all conditions, including minimum load conditions.
 