Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Minimum plate size for joist bearing on masonry

Status
Not open for further replies.

tolind

Civil/Environmental
Aug 19, 2003
30
I'm looking for a rule of thumb more than anything. I've calculated the required size of 6x6 for a joist bearing plate on masonry but everyone tells me that is smaller then they have seen. Does anyone know a general rule of thumb like "don't use less than a 6x10"?

Thanks for the help on this and everything else!

T
 
Replies continue below

Recommended for you

The minimum should be in your joist catalog or in the joist spec. If it works for bearing on the masonry and the thickness is sized correctly I see no reason to make it bigger. Our typical size is a 5x8 I think, that does give more area than the 6x6. You want wider so that there is less required precision in the plate placement. If it's off by an inch or two it won't kill you.
 
No rule of thumb needed - the Steel Joist Institute states the (nominal) minimum requirements in their specification. You can download the specification (free .pdf version), "41st Standard Specifications & Load Tables For Steel Joists & Joist Girders" from this link
You will have to register to get it, but I have not seen any "consequences" to registration since doing so last year.

For K-Series: 4"x6", see page 17

For LH- & DLH- Series: 6"x9", see page 48

For Joist Girders: 6"x9", see page 67

The bearing stress on the masonry & plate thickness have to be determined in accordance with AISC (ASD) requirements. Smaller bearing plates are allowed with certain restrictions.


 
Status
Not open for further replies.

Part and Inventory Search

Sponsor