Minimum PVC cover 1

Status
Not open for further replies.

scoute

Civil/Environmental
Jul 1, 2003
1
We are installing 4 inch schedule 40 PVC in an electrical substation at a depth of 30 inches below grade. The purpose of the pipe is to serve as a conduit for electrical relay cables. There will be some heavy traffic driveing over the conduit on a regular basis. I need an equation that will give me the maximum live load, (over the top of the pipe)assuming 90% compaction of fill, or minimum cover necessary
to facilitate heavy semi-trucks moving in the yard.
 
Replies continue below

Recommended for you

This information should be availabble from the pipe maker in the form of maximum and minimum cover tables. 30 inches is probably OK though.
 
I doubt that you will have any problems - after all, the top of the pipe will be more than 6 pipe diameters below ground. But if pipe failure is a serious concern and you can't put the pipe any deeper, then you might consider backfilling the trench with lean concrete. Stop the concrete 6 to 12 inches from the ground surface - then put base in the top of the trench.

[pacman]

Please see FAQ731-376 for great suggestions on how to make the best use of Eng-Tips Fora.
 
Let me first say at 30 inches down you should be ok. The 4 main references you need are by: The Boussineq Formula = Soil pressure stress = 0.477W/H squared. 2nd: Handbook of PVC Pipe Design: 3rd: Refer to Dr.Reynold Watkins Experiments on Buried Coduits. 4th AASHTO Specs. Good Luck.
 