Minimum rating of oil cooled transformer

Status
Not open for further replies.

power2020

Electrical
Aug 18, 2005
127
Dear Folks,
what is the minimum rating of Distribution transformer (11/0.415kV) requires to provide oil sump? And which standard gives this information.
Advanced thanks for your information.
 
Replies continue below

Recommended for you

Look in NFPA. I remember the stipulation is not based on transformer rating but on oil quantity, if oil quantity exceeds 2000 litres, sump needs to be provided.
 