PrebenJakobsen
Electrical
- Dec 1, 2008
- 27
When calculating minimum SC value on the output side of a UPS I don't think we can use the normal IEC60909 approach.
Inverter current will be limited:
When bypass is not available the inverter alone shall supply the SC.
If SC occurs close to the UPS the impedance in the loop is low, and the inverter will limit the current by reducing the voltage. The inverter is an active component and the internal impedance is un-linear and will adjust according to SC conditions.
If the SC occurs at the end of a long cable the current will be in the range where the inverter is able to supply it, and the output voltage will be kept at nominal level. The inverter internal impedance will be zero.
(Above considerations is valid for the first e.g. 150ms where the inverter can supply e.g. 230% of nominal)
Load current to other consumers will remain:
UPS systems are typically used for computer equipment with power supply that will operate on e.g. 50% voltage. During SC the voltage is low but the entire load in fault free branches will remain consuming power.
Both phenomena's will reduce the current available to trip the MCB in the faulty branch which is critical due to discrimination.
Does anyone know literature that describes how to calculate minimum SC on a UPS system?
Preben Jakobsen
Denmark
Inverter current will be limited:
When bypass is not available the inverter alone shall supply the SC.
If SC occurs close to the UPS the impedance in the loop is low, and the inverter will limit the current by reducing the voltage. The inverter is an active component and the internal impedance is un-linear and will adjust according to SC conditions.
If the SC occurs at the end of a long cable the current will be in the range where the inverter is able to supply it, and the output voltage will be kept at nominal level. The inverter internal impedance will be zero.
(Above considerations is valid for the first e.g. 150ms where the inverter can supply e.g. 230% of nominal)
Load current to other consumers will remain:
UPS systems are typically used for computer equipment with power supply that will operate on e.g. 50% voltage. During SC the voltage is low but the entire load in fault free branches will remain consuming power.
Both phenomena's will reduce the current available to trip the MCB in the faulty branch which is critical due to discrimination.
Does anyone know literature that describes how to calculate minimum SC on a UPS system?
Preben Jakobsen
Denmark