SprinklerDesigner2
Mechanical
- Nov 30, 2006
- 1,244
So that you all know I feel I am not competent when it comes to NFPA #30 and I have hired an FPE to help with the design criteria for this project. That said I am not looking for any specific design criteria as I will probably be getting that on Friday or early next week.
What I am asking of those who do have some experience is does it look like we will have enough water given the following:
1. Water supply is 1,250 @ 100 psi fire pump from city connection. At churn we had 170 psi, 1,250 gpm @ 140 psi and 1,900 gpm @ 110 psi. Very flat curve and I recognize the 1,900 gpm is over the 150% but that is what I got.
2. Building is bent metal purlin 24'-0" eave and 31'-4" at peak.
3. Commodity stored on back to back racks without shelves sine three and some four tiers high. Looks like we can expect storage 20' high.
4. There is a list of 530 chemicals being stored and just a small representative sample is provided below:
Looks like lots of required information is missing from that list but that is what I got and this is why I hired an experienced FPE to make sure I don't step in it.
From my amateur status going over NFPA #30 it appears the pump can't deliver enough water. I am not looking for any sort of definitive answer, like I said I will have that at the end of the week, but do you tend to agree with me from what your experience tells you?
Thanks.
What I am asking of those who do have some experience is does it look like we will have enough water given the following:
1. Water supply is 1,250 @ 100 psi fire pump from city connection. At churn we had 170 psi, 1,250 gpm @ 140 psi and 1,900 gpm @ 110 psi. Very flat curve and I recognize the 1,900 gpm is over the 150% but that is what I got.
2. Building is bent metal purlin 24'-0" eave and 31'-4" at peak.
3. Commodity stored on back to back racks without shelves sine three and some four tiers high. Looks like we can expect storage 20' high.
4. There is a list of 530 chemicals being stored and just a small representative sample is provided below:
Looks like lots of required information is missing from that list but that is what I got and this is why I hired an experienced FPE to make sure I don't step in it.
From my amateur status going over NFPA #30 it appears the pump can't deliver enough water. I am not looking for any sort of definitive answer, like I said I will have that at the end of the week, but do you tend to agree with me from what your experience tells you?
Thanks.